11-15-2024, 11:04 AM | #1 |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
Nuisance tripping when using BMW Flex Charger with NEMA 1-50 Receptacle with GFCI
As the title states. We have a new iX 50 and are running into issues with nuisance trips with the Flex Charger. The charger is plugged into a NEMA 14-50 that is connected to a 50A GFCI breaker.
Nuisance trips are not uncommon and it is typically suggested to hardwire the charger and use a standard breaker. With that said, we are renting for a few more months while we await completion of a new home. I'm debating swapping the GFCI breaker for a standard one just for the time being - in the new house, we will hard wire the charger. Have folks encountered similar issues? Wiring is definitely OK and we had no issues with our Q5 PHEV. Maybe the BMW chargers are more sensitive. Lowering the current limit makes no difference, and the breaker is warm (to be expected), but never hot. |
11-15-2024, 12:20 PM | #2 | |
Colonel
![]() 3174
Rep 2,432
Posts |
Quote:
|
|
Appreciate
0
|
11-15-2024, 12:23 PM | #3 |
Colonel
![]() 3938
Rep 2,248
Posts
Drives: ix xDrive50
Join Date: Jul 2023
Location: Georgia
|
Portable EVSEs must have CFCI. That is the problem - the code requirement dictates that we have cascaded GFCIs. Another reason that hardwire is superior - only a single GFCI in the flow.
__________________
2024 iX xDrive50 Phytonic Blue on Mocha with DAPP, Premium, B&W, Ventilated & Radiant Heated Seats, Adaptive Headlights, and Luxury
|
Appreciate
0
|
11-15-2024, 01:17 PM | #4 |
Major
![]() 1773
Rep 1,153
Posts
Drives: 2025 BMW iX 50
Join Date: Jan 2023
Location: Los Angeles
|
Have you tried reducing the maximum Current Limit for AC Charging in your My BMW app/car? Maybe you can just put it down to a lower number such as 12A or 18A in the meantime so it won't overload the circuit?
|
Appreciate
1
RichardInCA6472.50 |
11-15-2024, 01:53 PM | #5 |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
The latest NEC calls for all 240V receptacles in a garage must have a GFCI breaker. But yea I suspect this is the exact issue - there are two GFCI in the chain and this is causing the breaker to trip.
With that said I would normally hardwire but this is a rental and we will only be here for a few months. Is it definitely true that the Flex Fast Charger has its own GFCI? If so I do think I’ll swap with a standard breaker for now. Yes I have tried reducing current but still having issues. |
Appreciate
1
exxxviii3938.00 |
11-15-2024, 03:04 PM | #6 | |
Colonel
![]() 3174
Rep 2,432
Posts |
Quote:
Can I install ChargePoint Home Flex on a GFCI breaker? Yes. However, if local codes require a GFCI breaker for plug-in installation, ChargePoint recommends a hardwire installation. We do not recommend using a GFCI breaker as the Home Flex already has integrated charging circuit interrupting device (CCID) protection. Using a GFCI breaker in the panel, especially with a plug-in installation, can cause nuisance breaker tripping in certain circumstances and interrupt charging. |
|
Appreciate
0
|
11-15-2024, 03:09 PM | #7 | |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
Quote:
And yes this would be swapped back with the GFCI when we leave. The owner of the unit had done some electrician work in his past and was OK with the proposal. I'd still like to know if the BMW Flex charger specifically has its own GFCI. I cannot find anything saying specfically it does. |
|
Appreciate
0
|
11-15-2024, 09:26 PM | #8 |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
Well I swapped the breaker with a standard 50A and was able to get all the way to 80% (my set limit) with no issues. I'm confident this is due to the nuisance tripping referenced above. I still cannot find details on the GFCI protection inside the Flex charger itself - I definitely don't see a reset button, but the NEC also dictates all EVSE shall have GFCI...
This will do until we move into the new house with a proper hardwired charger. |
Appreciate
1
thebishman1728.50 |
11-18-2024, 11:57 AM | #9 | |
Captain
![]() ![]() ![]() ![]() 1110
Rep 856
Posts |
Quote:
|
|
Appreciate
1
sarugby4life433.00 |
11-18-2024, 12:09 PM | #10 |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
|
Appreciate
0
|
11-18-2024, 12:19 PM | #11 |
Captain
![]() ![]() ![]() ![]() 1110
Rep 856
Posts |
|
Appreciate
0
|
11-18-2024, 12:45 PM | #12 |
Lieutenant
![]() ![]() ![]() 433
Rep 543
Posts |
Yes this is true. CA is always trying to do everything first 😂
|
Appreciate
1
Maverick2411109.50 |
11-19-2024, 07:35 AM | #13 | |
Colonel
![]() 4244
Rep 2,555
Posts |
Quote:
Also, a garage is not considered an outdoor space. It's considered an indoor space even though it is not liveable square footage. GFIs are only required in outdoor/wet areas. The garage is neither of those. |
|
Appreciate
1
sarugby4life433.00 |
11-19-2024, 01:15 PM | #14 | |
Lieutenant Colonel
![]() 2182
Rep 1,780
Posts
Drives: 2023 iX xDrive50
Join Date: Nov 2011
Location: Seattle
|
Quote:
“GFCI protection is required for outdoor outlets rated 50 amp or less in garages and for outlets rated not over 150 volt to ground, 50 amp or less in accessory buildings and boathouses.”
__________________
Past BMW's
2020 M850i GC | 2020 X5 | 2018 M550i | 2017 X5 | 2014 535d | 2013 X5 | 2007 530i | 2002 X5 | 2000 540i/6 | 1999 M Roadster | 1989 535i | 1984 533i | 1983 533i | 1977 530i |
|
Appreciate
0
|
11-19-2024, 01:33 PM | #15 | |
Colonel
![]() 3174
Rep 2,432
Posts |
Quote:
Also, "bringing it up to code" is all subjective as you had mentioned but if his electrician is pulling a permit to install that 50A circuit, then he will fail the inspection if he doesnt put the GFCI breaker. He can bypass it by not pulling the permit and dealing with it later when he is trying to sell the house by claiming ignorance as the home inspector will point these out to be fixed before buying the house and its upto the buyer to enforce it or not |
|
Appreciate
1
LVBMW4771.50 |
11-19-2024, 07:15 PM | #16 | |
Captain
![]() ![]() ![]() ![]() 1110
Rep 856
Posts |
Quote:
|
|
Appreciate
0
|
11-19-2024, 07:17 PM | #17 |
Colonel
![]() 3174
Rep 2,432
Posts |
Right if you are hardwiring the EVSE. If you have an outlet that means you can plug anything in it. You may just use it for EVSE but who knows what the person coming after you is gonna plug in. Thats why the GFCI requirement. There is no telling what the plug is being used for from a code standpoint
Last edited by Aalfred; 11-19-2024 at 07:18 PM.. |
Appreciate
1
Maverick2411109.50 |
11-20-2024, 07:49 AM | #18 | |
Colonel
![]() 4244
Rep 2,555
Posts |
Quote:
|
|
Appreciate
0
|
11-20-2024, 08:22 AM | #19 |
Colonel
![]() 3174
Rep 2,432
Posts |
Are you talking about plugging it into an outlet (receptacle) or hardwiring it? If it hardwiring, then yes. If its plugging it into an outlet, then NO unless you can cite something that says otherwise.
|
Appreciate
0
|
11-20-2024, 08:26 AM | #20 |
Colonel
![]() 3938
Rep 2,248
Posts
Drives: ix xDrive50
Join Date: Jul 2023
Location: Georgia
|
__________________
2024 iX xDrive50 Phytonic Blue on Mocha with DAPP, Premium, B&W, Ventilated & Radiant Heated Seats, Adaptive Headlights, and Luxury
|
Appreciate
0
|